PostPosted: Sun Feb 14, 2010 11:23 am    Post subject: Reply with quote

Faulty equipment shouldn't be out there being used ...?
All people should be healty,but they are not.Practicaly it is not the same when you have bin of 20 leads,and bin of 600 leads on side.
It is not the same when you see build up and pull out and damage
in and out on the equipement.What is the point of tagging of good equipement?No point at all,exept the residue of glue from test tag.
But there is a need for clear enforcement for dealing with faulty equipement and we need prohibition tag .End of story.
Back to top
View user's profile Send private message
RoderickvG



Joined: 13 Mar 2006
Location: Sydney

PostPosted: Sun Feb 14, 2010 12:18 pm    Post subject: Reply with quote

That is the biggest load of bulls*** I have seen in a long time.
There is NO EXCUSE for using faulty equipment, ever.
If you can't manage the job safely, find another occupation.

And that's the end of story!
_________________
Think it is too expensive to hire a professional, wait until you hire an amateur
Back to top
View user's profile Send private message Visit poster's website
beatsonic



Joined: 11 Jan 2004
Location: Malaga, Western Australia

PostPosted: Sun Feb 14, 2010 3:42 pm    Post subject: Reply with quote

i cant believe that i just read that!
how much value do you put on your life, and more the point, on the life of your colleges and friends f9!?!
would you be prepared to stand infront of a coroner in court at the enquest into a death you caused and say "i thought it would be okay to use something i knew that was faulty"
there is just no excuse for using faulty equipment, ever!
_________________
Craig
craig@illusionlighting.com.au
www.illusionlighting.com.au
Back to top
View user's profile Send private message Send e-mail Visit poster's website MSN Messenger
f9



Joined: 27 Mar 2007
Location: Sydney

PostPosted: Sun Feb 14, 2010 7:42 pm    Post subject: Reply with quote

Your opinions just give strength for need of Prohibition tag.
I am more practical and realistic. I don’t fly in perfect world of super taggers. I have same concerns like you but I see practical solution in elimination of irresponsibility.
If anyone with authority put prohibition tag-end of story means out of service .What it is the point to mark good and tested equipment and don’t mark faulty one? No point at all.
No dodgy owners of electrical equipment, no sneaky managers with business interest before safety, no more lazy electrical personnel which can use spit for insulation. No more professional Test- taggers which forget the testing part and work on gluing part, dates, Permanent Markers, license numbers etc.
100% I am against using faulty equipment anyway and that is reason asking for prohibition tag with enforcement procedure so you guys cool down.
By the way ...don’t kill the messenger. If you want reality show
I can make easy. Just I will get one camera and go around some events and bring to screen real-deal. You can be shocked with reality.
Last week, I have seen test tag from person with electrical license who newer test the equipment. Someone else has done crime using his data. Names and license numbers can be found on web of Office of Fair Trading NSW and tags purchased from Electrical wholesalers. This is widespread in Exhibition industry from customers who bring their own equipment and don’t want to pay for Electrician to test their equipment. They have a tag and they have faulty equipment tagged.
You have to be Sherlock Holmes? Who can police this? No one!
Back to top
View user's profile Send private message
Don Allen



Joined: 19 May 2003
Location: Perth Western Australia

PostPosted: Mon Feb 15, 2010 12:23 am    Post subject: Reply with quote

From the draft 3760:

2.4 Action resulting from inspection and testing
2.4.1 Non-compliant equipment
Where in-service inspection or testing identifies equipment which fails to comply with the criteria given in this Standard, the equipment shall be appropriately labelled to indicate that the equipment requires remedial action and warn against further use. Such equipment shall be withdrawn from service. The choice of remedial action, disposal or other corrective action shall be determined by the owner or the person responsible for the safety of the site.

As the standard says, use an appropriate label such as http://www.unisa.edu.au/ohsw/images/outofservice.JPG

Cowboys have turned testing and tagging into a sham, but our industry is a responsible industry overall and is actively seeking to ensure unsafe electical equipment is taken out of service.

ALIA members have been actively involved in the update and evolution of 3760, so that it becomes part of an active safety environment, which includes continous visual inspections and a testing and tagging program.

The concept of assuming that every piece of electrical equipment is safe unless it has a prohibition label is a defective safety program as an untrained user has no way of knowing which item of equipment is included in your defective testing program.
_________________
Lighting Designer and manufacturer of Theatre Electronics
Back to top
View user's profile Send private message
f9



Joined: 27 Mar 2007
Location: Sydney

PostPosted: Mon Feb 15, 2010 8:33 am    Post subject: Reply with quote

The concept of assuming that every piece of electrical equipment is safe unless it has a prohibition label ....is not my concept.Draft is
perfect.This way enforcement can be done with enforcement label
on identified faulty equipement.
I am not at all against mandatory periodical testing and tagging.
Back to top
View user's profile Send private message
GL



Joined: 29 Dec 2009

PostPosted: Sun Mar 07, 2010 11:34 pm    Post subject: Reply with quote

f9 wrote:


Your opinions just give strength for need of Prohibition tag.



An Out of Service tag is the preferred method... though the most effective, readily available method, which has been in use for quite a while now... is to remove/ cut the male plug off the damaged item - so it can't be used and has to be fixed. Wink
_________________
"No matter what age we are, some have never quite left the schoolyard"
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    ALIA Online Forum Index -> Current Affairs All times are Australian EST (GMT + 10hrs)
Goto page Previous  1, 2
Page 2 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum


Powered by phpBB © 2001, 2005 phpBB Group
ALIA theme adapted by Andy Ciddor from subSilver by subBlue design
All content is © Copyright Australasian Lighting Industry Association (Incorporated), 2003-2004